防火门是否必须向疏散方向开启?

建筑中的储藏间、小库房、污洗污存等房间门按规范需要采用防火门,当这些房间的使用人数不大于60人,且平均每樘门的疏散人数不大于30人时,是否可以按照《建筑防火通用规范》GB55037-2022第7.1.6条的规定,防火门朝内开启?

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

潘天坤 2024-07-12 18:17 10 [回复]举报

每樘门是平均疏散人数要求

其他建筑中使用人数不大于60人的房间或每樘门的平均疏散人数不大于30人的房间的疏散出口门可以不向疏散方向开启

leap21 2024-07-13 07:35 00 [回复]举报

满足条件可以向内开

LHH2737 2024-07-13 09:34 00 [回复]举报

没有防火门必须朝哪边开启这种规定,但是如果是配电间的防火门必须朝疏散方向开启

一棵树而已   回复: LHH27372024-07-17 17:02

哪条规定的?求告知

0    0 [回复]举报

LHH2737   回复: 一棵树而已2024-07-18 14:08

GB 50053-2013第6.2.2条,变压器室、配电室、电容器室的门应向外开启。相邻配电室之间有门时,应采用不燃材料制作的双向弹簧门。

0    0 [回复]举报

周家斌 2024-07-13 17:10 00 [回复]举报

phone0224 2024-07-15 10:22 00 [回复]举报

可以的