消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问1.76MPA的水泵可用1.6MPA的管件吗

项目消防水泵为1.76MPA,管件为1.6MPA,泄压阀动作压力设计为1.4MPA,个人认为管件1.6MPA不符合要求,假如泄压阀故障水泵启动压力会超过1.6MPA,超过管件的额定工作压力会有安全隐患。请各位老师帮解答,最好能有相关规范,万分感谢!

南飞野雁 | 2024-06-29 22:02
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

消防网友68723 2024-07-01 09:54 20 [回复]举报

GB50974,8.2.1 消防给水系统中采用的设备、器材、管材管件、阀门和配件等系统组件的产品工作压力等级,应大于消防给水系统的系统工作压力,且应保证系统在可能最大运行压力时安全可靠。

8.2.3 高压和临时高压消防给水系统的系统工作压力应根据系统在供水时,可能的最大运行压力确定,并应符合下列规定:
    1 高位消防水池、水塔供水的高压消防给水系统的系统工作压力,应为高位消防水池、水塔最大静压;
    2 市政给水管网直接供水的高压消防给水系统的系统工作压力,应根据市政给水管网的工作压力确定;
    3 采用高位消防水箱稳压的临时高压消防给水系统的系统工作压力,应为消防水泵零流量时的压力与水泵吸水口最大静水压力之和;
    4 采用稳压泵稳压的临时高压消防给水系统的系统工作压力,应取消防水泵零流量时的压力、消防水泵吸水口最大静压二者之和与稳压泵维持系统压力时两者其中的较大值。

LHH2737 2024-07-01 15:45 10 [回复]举报

你是对的,GB 50974-2014第8.2.1 消防给水系统中采用的设备、器材、管材管件、阀门和配件等系统组件的产品工作压力等级,应大于消防给水系统的系统工作压力,且应保证系统在可能最大运行压力时安全可靠。8.2.3 高压和临时高压消防给水系统的系统工作压力应根据系统在供水时,可能的最大运行压力确定

潘天坤 2024-07-01 18:18 10 [回复]举报

管材公称压力PN和工作压力的关系,从规范来说还不太好入手(例如PN16的产品,能否使用在1.3MPa位置)

楼主举的这个例子,水泵参数已经大于公称压力了,理论上可以根据楼上两位老师发的规范内容提出违反条款

3211233 2024-07-02 14:35 00 [回复]举报

泵如果工况点压力为1.76MPa,那么在刚起泵,0流量时压力大概在2.4MPa左右,早超1.6MPa了

Aris_Ji 2024-07-02 17:01 00 [回复]举报

这个不仅要看工作压力,你还需考虑管道强度试验压力+0.4Mpa

关闭

关闭

手机APP下载