消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

风机房可以设在二楼,然后通过竖风井对2层以上的楼层进行排烟吗

风机房可以设在二楼,然后通过竖风井对2层以上的楼层进行排烟吗,如果可以的话,那会有什么另外要求吗比如风机排烟量是否要增加

K先生 | 2021-11-14 23:07
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

一片冰雨 2021-11-15 04:28 20 [回复]举报

4.4.4 排烟风机宜设置在排烟系统的最高处,烟气出口宜朝上,并应高于加压送风机和补风机的进风口,两者垂直距离或水平距离应符合本标准第3.3.5条第3款的规定。

没有绝对必要的情况!从底下排烟,恐怕不行!

刘丽波 2021-11-15 06:31 20 [回复]举报

烟规规定排烟风机宜设于上部。对于这种倒排方式也是可以的,只是不理想。有些地标也有要求,但风量不需要增加,排烟出口尽量设于上部。

小马 2021-11-15 11:59 20 [回复]举报

还真见过有主体这样设计的,是办公楼。

但是烟都是往上走的,能在顶层设置还是在顶层设

GANSTER 2022-02-10 16:44 20 [回复]举报

系统设计,底部排烟主要是要考虑烟囱抽力的影响,需要校核风机压头。但还要考虑底部排烟烟气会有倒灌至上部建筑的可能,因此一般不建议底部排烟,特别是楼层较多的情况,一旦蔓延至上面楼层造成损失,设计人吃不了兜着走!有人会说地下室排烟也会出现这种情况,但地下室排烟风机是在地下室排烟系统最高处,暖通设计至少是合规的。

关闭

关闭

手机APP下载