柴油发电机房消防设施的选型

柴油发电机房有强制规定使用那种类型的自动灭火设施吗,是必须使用气体灭火系统吗?

陈守成 | 2024-12-24 10:49
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

潘天坤 2024-12-24 14:15 00 [回复]举报

请问是设置在什么建筑内,还是独立建造的柴油发电机房?

建筑内有设置自动喷水灭火系统嘛?


柴油发电机本身及其储油设施具有一定的火灾危险性,因此柴油发电机房应设置必要的灭设施。柴油发电机房内的灭火设施选择,应根据发电机组的大小、数量、用途等实际情况确定(布置在民用建筑内的柴油发电机房应设置与柴油发电机容量和建筑规模相适应的灭火设施,当建筑内其他部位设置自动喷水灭火系统时,机房内应设置自动喷水灭火系统;对于容量大、规模大的多层建筑以及高层建筑,需设置自动灭火系统;对于按照规范要求设置自动喷水灭火系统的建筑,建筑内设置的燃油、燃气锅炉房等房间也要相应地设置自动喷水灭火系统;对于未设置自动喷水灭火系统的建筑,可以设置推车式ABC干粉灭火器或气体灭火器,如规模较大,则可设置水喷雾、细水雾或气体灭火系统等)


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据

有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准


陈守成   回复: 潘天坤2024-12-24 16:20

设置在多层公共建筑内,建筑内设有自动喷水灭火设施但柴油发电机房未设置灭火设施关于灭火设施选型可以强调必须选择气体灭火设施吗?


0    0 [回复]举报

潘天坤   回复: 陈守成2024-12-24 18:31

如果不属于规模特大的情况,设计也没有特别要求,可以选择自动喷水灭火系统,当然想要采用水喷雾、细水雾或气体灭火系统也是可以的

0    0 [回复]举报