消防灯具的IP等级要求是多少?

发布于:2024-10-09 19:58

消防应急照明和疏散指示系统技术标准 GB51309-2018

 

    3.2.1 灯具的选择应符合下列规定:

    7 灯具及其连接附件的防护等级应符合下列规定:       

    1)在室外或地面上设置时,防护等级不应低于IP67;       

    2)在隧道场所、潮湿场所内设置时,防护等级不应低于IP65;       

    3)B型灯具的防护等级不应低于IP34。

 

建筑电气与智能化通用规范 GB55024-2022

 

    4.5.3 室外灯具防护等级不应低于IP54,埋地灯具防护等级不应低于IP67,水下灯具的防护等级不应低IP68。

 

公园设计规范 GB51192-2016

 

    10.4.2 安装在室外的灯具外壳防护等级不应低于IP54;埋地灯具外壳防护等级不应低于IP67;水下灯具外壳防护等级不应低于IP68;室外灯具的接线盒防护等级不应低于IP54。            

    10.4.3 室外灯具、镇流器箱分线盒(箱)之间的电线(缆)应采用配件齐全的防水防腐型可绕金属软管,两端锁母应与导管配套,安装后不应脱落。