关于消防检测问题。

就是被检测单位是只是在建筑里一层或部分楼层是。检测单位仍需对公共部分设备都要检测吗?还是在被检测单位内检测相关设备符合规定就好。(例如消火栓静压和动压,是否为检测区域内符合要求就好。)

黄伟强 | 2024-05-31 19:34
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

懒得说 2024-06-01 07:52 00 [回复]举报

消防第三方检测不只是对消防设施功能性检测

我头发贼黑 2024-06-01 08:21 00 [回复]举报

公共区域相应功能得能实现,就像你说的动压测试,需要启动消防泵的,其他的也一样

王宇晗 2024-06-01 10:31 00 [回复]举报

主要还得看合同内约定的检测范围,如合同内约定只对一个建筑物内的部分楼层进行检测的话,其余部分不用管,但是这个检测报告不能用于这个建筑物整体,也就是说这个建筑物一年内还得有一次整体的消防检测

风间澈 2024-06-01 11:34 00 [回复]举报

检测报告需要保证消防设施系统的完整性要求,如共用的消防泵,火灾报警控制器,共用的排烟风机等功能要符合相关要求

潘天坤 2024-06-16 13:51 00 [回复]举报

个人认为:建设工程消防验收(备案)前的消防第三方检测服务应该将设计范围内的内容完成,然后非设计范围内的内容(例如阴影部分的公共疏散走道)如果故障,也可以提出但备注利旧等(不是强制性,能做到更好)。

如果是原有消防水泵、消防风机等设施故障,影响了设计范围内的功能,也应该提出整改,至少保障设计范围内功能正常。