一个防火分区内同时设置了自动喷淋系统与自动消防炮

一个防火分区内同时设置了自动喷淋系统与自动消防炮(两种消防设施界限有墙体分隔),消防泵合用需要合并计算设计流量吗?

凉饭 | 2024-05-29 16:05
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 4

消防网友62179 2024-05-30 01:37 00 [回复]举报

字面意思  一个防火分区   然后墙体分隔     如何划分的防火分区呢  

同一防火分区  需要合计

一路同行 2024-05-30 08:21 30 [回复]举报

9.1.7 建筑内设有不同类型的系统或有不同危险等级的场所时,系统的设计流量应按其设计流量的最大值确定。

南明离火 2024-05-30 09:14 10 [回复]举报

只要不是同时工作就不用

黄-江西省景德镇市 2024-06-02 11:55 00 [回复]举报

如果两个系统的灭火覆盖范围有交集就必须合并计算流量,若完全无交集就按流量较大的系统计算,且不能低于水炮的最低工作压力。