消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

不能联动启动排烟风机的情况

各位老师好:        排烟风机手动可以启动,打到自动状态后做联动试验,触发一个烟感,按下一个手报,对应排烟风阀自动打开,但风机不能联动启动。继续做试验,换了一个防烟分区,触发两个烟感,对应排烟风阀自动打开,风机没有启动。        麻烦问一下原因。

牛奶面包蛋 | 2024-05-10 08:14
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

香.香 2024-05-10 10:06 20 [回复]举报

首先知道排烟风机的联动开启过程:触发同一防烟分区的两个独立探测器(实际施工也有一探+一手),报警主机收到信号后联动打开排烟阀。排烟阀开启后反馈信号给主机,主机再联动开启风机。你现在的问题是接收到信号后排烟阀开启了风机没有启动。第一步先检查排烟阀的开启信号有没有反馈到主机,比如模块和信号线有无问题。如没有问题你再查看主机与风机之间的模块和线路有没有问题。一般就是这里出现了问题。

蜗牛仔仔 2024-05-10 11:00 00 [回复]举报

1.联动程序是否有问题:A火警启风阀,风阀启风机,B火警启风阀和风机。

2.如果是A类程序,检测风阀的反馈信号有没有收到。

3.风机的多线盘有没有开启自动

牛疼 2024-05-10 15:39 10 [回复]举报

风机没有参加联动

具体产生的原因有很多,逻辑未编写,缺少联动模块等

关闭

关闭

手机APP下载