泡沫-水雨淋系统设计流量计算

我们在设计仓库泡沫-水雨淋系统中,对系统的设计流量计算与施工图审查单位意见有些出入,希望专家对GB50151-2021《泡沫灭火系统技术标准》中相关条款给予解答。

2000平方的丙类液体仓库,泡沫-水雨淋按日子型布置,设6组雨淋阀,系统设计流量按同时开启两组雨淋阀考虑,设计流量约100L/s,设计依据是GB50151-2021《泡沫灭火系统技术标准》8.1.3条及GB50084-2017《自动喷水灭火系统设计规范》9.1.9条及其条文解释。图审单位认为GB50151-2021《泡沫灭火系统技术标准》6.2.1条中泡沫-水雨淋系统的保护面积应按保护场所内的水平面面积或水平投影面积确定,也就是说在保护面积范围内所有的雨淋阀都要开启,也即本项目系统设计流量需要按同时开启6组雨淋阀计算,设计流量约300L/s。我们想知道图审单位的解释是否正确?

头文字X | 2024-04-10 16:09
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

xzn87 2025-05-08 09:33 00 [回复]举报

我觉得严格来说图审解释是没问题的,但很多场所为了降低流量和造价,采用人为分区按同时动作的雨淋阀来计算流量也是合理的,你这个项目按着火区域和相邻区域同时动作的话应该需要按三台雨淋阀考虑吧