请教各位大神,有一个戊类工业建筑,室外消防设计流量15L/S,室内消防设计流量10L/S,室内栓数量大于10个,采用干式消火栓系统,根据50974-8.1.5条,室内消防管网一定要设置成环状吗?图集19S401-83页说管网应成支状,以哪个为准呢?

王舜 | 2023-12-07 20:02
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-12-08 09:01 10 [回复]举报

是否需要成环与干式、湿式无关,图集是规范的条文说法的解决方案,如果规范与图集不符的话,从法理上贵伐效力强于图集


消防给水及消火栓系统技术规范 GB50974-2014


8.1.5 室内消防给水管网应符合下列规定:    

1 室内消火栓系统管网应布置成环状,当室外消火栓设计流量不大于20L/s,且室内消火栓不超过10个时,除本规范第8.1.2条外,可布置成枝状;    

2 当由室外生产生活消防合用系统直接供水时,合用系统除应满足室外消防给水设计流量以及生产和生活最大小时设计流量的要求外,还应满足室内消防给水系统的设计流量和压力要求;    

3 室内消防管道管径应根据系统设计流量、流速和压力要求经计算确定;室内消火栓竖管管径应根据竖管最低流量经计算确定,但不应小于DN100。


8.1.2 下列消防给水应采用环状给水管网:    

1 向两栋或两座及以上建筑供水时;    

2 向两种及以上水灭火系统供水时;    

3 采用设有高位消防水箱的临时高压消防给水系统时;    

4 向两个及以上报警阀控制的自动水灭火系统供水时。


平常o 2023-12-08 13:38 00 [回复]举报

19S401?  有吗

王舜   回复: 平常o2023-12-09 12:38

图集里83页干式消火栓系统提到了管网布置,你可以看看

1    0 [回复]举报