消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水泵房内管道与设备的连结方式

消防泵的吸水管,出水管与闸阀,止回阀,泄压阀的连结方式必须采用法兰连接嘛,是否可以采用沟槽

冷风 | 2023-11-25 16:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

安洪全 2023-11-27 08:55 00 [回复]举报

看管径和系统压力

消防给水及消火栓系统技术规范 GB50974-2014

8.2.5 埋地管道当系统工作压力不大于1.20MPa时,宜采用球墨铸铁管或钢丝网骨架塑料复合管给水管道;当系统工作压力大于1.20MPa 小于1.60MPa时,宜采用钢丝网骨架塑料复合管、加厚钢管和无缝钢管;当系统工作压力大于1.60MPa时,宜采用无缝钢管。钢管连接宜采用沟槽连接件(卡箍)和法兰,当采用沟槽连接件连接时,公称直径小于等于DN250的沟槽式管接头系统工作压力不应大于2.50MPa,公称直径大于或等于DN300的沟槽式管接头系统工作压力不应大于1.60MPa。


8.2.9 架空管道的连接宜采用沟槽连接件(卡箍)、螺纹、法兰、卡压等方式,不宜采用焊接连接。当管径小于或等于DN50时,应采用螺纹和卡压连接,当管径大于DN50时,应采用沟槽连接件连接、法兰连接,当安装空间较小时应采用沟槽连接件连接。

消防网友8198 2023-11-27 09:21 20 [回复]举报

产生负压的管道不能采用沟槽连接

关闭

关闭

手机APP下载