消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防排烟风机控制箱内部空开是否设置错误。

低压配电设计规范 GB50054-2011 6.3.6 过负荷断电将引起严重后果的线路,其过负荷保护不应切断线路,可作用于信号。

此条规范要求消防排烟风机控制箱出现过负荷时,不应自动断电跳闸。但是日常中,很多排烟风机控制箱内部都有断路器,且断路器有过载保护功能,请问是否厂家设置错误。

深圳消防 | 2023-08-16 10:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 3

无名之辈 2023-08-17 11:40 00 [回复]举报

热磁保护3300不行,单磁保护3200可以

周家斌 2023-08-17 13:46 00 [回复]举报

大两倍过负荷参数是可以的,也可以用3200系列的

潘天坤 2024-06-21 00:41 00 [回复]举报

请问型号是否一致,看现场照片是IC65N D40?

断路器型号太多了,如果没有标记内容,不太好分辨断路器具体有什么功能,可能还需要厂家提供一些型号和功能证明


如果防排烟风机断路器有过负荷保护功能,是有问题的。


普通的配电线路应装设短路保护和过负荷保护;消防排烟风机及水泵的线路属于过负荷断电会引起严重后果的,过负荷保护只作用于信号不切断电源。

也就是说排烟风机应采用具有短路保护和过负荷报警而不切断电源的断路器。

关闭

关闭

手机APP下载