消控室值班要求

分消控室也需要24小时值班吗

炖小鱼 | 2023-06-08 08:49
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

周家斌 2023-06-08 09:35 00 [回复]举报

需要

安洪全 2023-06-08 09:38 00 [回复]举报

消防控制室通用技术要求 GB25506-2010

火灾自动报警系统设计规范 GB50116-2013

人员密集场所消防安全管理 GB/T40248-2021

我查了三本规范,均未对分控制室做出规定。

看看属地的地方管理标准或问问属地的管理部门什么要求,看能不能有折中方案,比如由保安兼任值班人员,或减少值班人数。

Demon Hunter 2023-06-08 09:56 10 [回复]举报

分消控室的报警主机若只是分机,且其信号已接入总消控室的总机,总机能显示和控制分机所连接的所有设备(特别是风机水泵的直启),那么分消控室就不需要设置值班了,在总消控室设置双人持证上岗24小时值班即可。