不充气单连锁预作用系统疑问

关于不充气的单连锁预作用系统,我有几个小疑问:
1、不充气单连锁预作用系统与传统的湿式系统区别之一在于报警阀不同(预作用相当于雨淋+湿式)和联动方式不同,前者比后者多了一道排气的工序(不充气的话是否还要排气?);
2、预作用系统的报警阀后的管路平时充满低压空气,当火灾传感器联动排气后,水才开始充满管道,但是如果喷头不破,也是不喷水的。并且预作用系统对于报警阀到最不利喷头的管段长度是有要求的(允许充水时间2min);
3、不充气单连锁预作用系统最不利端需要设置电磁排气阀,排气阀大小需根据报警阀后的管段排气量决定。不充气系统一般最不利配水管末端设置一个排气阀即可?

4、不充气的单连锁系统较充气单连锁系统,复位的时候是怎么样的一个流程?泄水后,是不是只是少了充气这个步骤?

小月半 | 2022-11-26 09:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

张牙舞爪的张 2022-11-26 10:47 10 [回复]举报


第一个问题:1、湿式系统联动启动方式分为自动启动、联锁启动。自动启动的信号是报警阀组压力开关和一路报警信号作为自动启动信号,与预作用系统自动启动信号是有所区别。2、不充气管道内部还是有空气,还需设置自动排气阀;管道充气则设置快速排气阀。

第二个问题:单联锁预作用系统满足两路报警信号后则启动预作用阀组电磁阀,水泵启动管网冲水,同时开启管道中自动排气阀的电动阀进行排气。喷头爆破后管道开始喷水,与管道冲水时间不冲突。

第三个问题:个人认为,与自动排气阀数量关系不大,满足管网冲水时间和管网排气要求即可。

四个问题:本人暂无能力解答,抱歉。


小月半   回复: 张牙舞爪的张2022-11-30 20:22

感谢!受教了!

0    0 [回复]举报