实验室装修隔墙不到顶

实验室装修,隔墙只到吊顶下,并没有到楼板或者梁下,铝扣板吊顶,这种情况可以吗?排烟怎么做?是按整个大空间考虑,还是隔完的每个房间独立考虑?

亮1103 | 2022-09-29 18:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

永锅 2022-09-30 08:42 00 [回复]举报

实验室应采用2.00h的防火隔墙和1.00h的楼板与其他场所或部位分隔。

隔墙应从楼地面基层隔断至梁、楼板或屋面板的底面基层。

排烟系统按每个小房间考虑。

gy建筑设计   回复: 永锅2023-04-17 20:58

我也困惑这个问题,并没有找到特殊赦免条款。看来只能到顶吗?

0    0 [回复]举报