仓库灯距规定是什么

根据公安部6号令第39条 库房内不准设置移动式照明灯具。照明灯具下方不准堆放物品,其垂直下方与储存物品水平间距离不得小于零点五米。而在《仓储场所消防安全管理通则》( XF1131-2014 )里第6.8条规定,物品与照明灯之间的距离不小于0.5 m;那到底是以哪个标准为准?照明灯具下是否可放置物品?

金木 | 2022-02-09 22:29
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

7R1CK5T3R 2022-02-10 13:46 20 [回复]举报

根据《公安部6号令》,照明灯具下方确实不准堆放物品。

注意看后面半句,“垂直下方与储存物品水平间距离不得小于零点五米”,这个和《仓储场所消防安全管理通则》里的“物品与照明灯之间的距离不小于0.5 m”其实是同一个意思。

这里所谓的距离讲的都是水平距离,是照明灯具到地面的垂线与货物之间的水平距离,不是照明灯具高度减去堆放货物高度后得出来的垂直距离。

因此,这两个法规标准之间并不冲突。

金木   回复: 7R1CK5T3R2022-02-10 16:23

谢谢!



《仓储场所消防安全管理通则》里8.3 仓储场所的电器设备应与可燃物保持不小于0.5 m的防火间距,架空线路的下方不应堆放物品。架空线放在桥架里受此约束吗?

0    0 [回复]举报

7R1CK5T3R   回复: 金木2022-02-10 17:32

确实,一般来说仓库内部的架空线路基本都不是干拉的,而是放在桥架内的,但我认为需要看情况。

架空线路下方不准放物品,主要是为了防止一旦线路起火,熔融的部分掉落到下方后引燃下方货物。

由于有一些桥架不是全封闭型的,尤其是有些桥架底面几乎是镂空的,这种就会有熔融部分容易引燃下方货物的风险。因此不建议在下方放置。

若桥架是全封闭的话,那么在下方放置也不是不行。

个人业余意见,仅供参考。

0    0 [回复]举报

金木   回复: 7R1CK5T3R2022-02-10 23:00

非常感谢

0    0 [回复]举报