排烟设施问题

地上厨房小于100平无窗,需要设置机械排烟吗?

消防网友52694 | 2022-01-24 11:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

@mad 2022-01-24 15:49 00 [回复]举报

       地上建筑内的无窗房间,当总建筑面积大于200m²或一个房间建筑面积大于50m²,且经常有人停留或可燃物较多时,应设置排烟设施。

ROY 2022-01-24 17:46 00 [回复]举报

楼上回复为GB50016第8.5.4条规定。厨房认定为经常有人停留或可燃物较多场所可能存在争议,个人认为应综合考虑厨房的设计用途及是否使用燃气、是否储存食用油等易燃物情况进行综合判定。

潘天坤   回复: ROY2024-07-03 15:20

厨房经常有人停留有什么争议呀?难道按照无人停留考虑?

0    0 [回复]举报

GANSTER 2022-02-10 10:52 00 [回复]举报

厨房至少满足人员经常停留这一条,因此必须考虑做排烟

潘天坤 2024-07-03 15:20 00 [回复]举报

此区域属于建筑面积大于50平方米且经常有人停留的无可开启外窗的房间,需要设置排烟设施,可以考虑增设可开启外窗或者机械排烟系统