消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防救援窗

1、一层或者二层的有窗建筑(丙类厂房和办公楼,是否还要设置消防救援口)   2、厂房的外墙推拉门或者卷帘门能否算做消防救援口

chentao820303 | 2025-06-11 17:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

罗马苏丹 2025-06-12 13:27 00 [回复]举报

消防救援口要求设置可在室内和室外识别的永久性明显标志,且应易于从室内和室外打开或破拆,推拉门和卷帘门不符合这些要求

牛丫头消防课堂 2025-06-13 01:06 10 [回复]举报

依据《建筑防火通用规范 》GB55037-2022,如果每层都有窗,一层二层可以不设置救援窗;

第二个问题,推拉门如果尺寸能满足要求,可以使用。

但是卷帘门能否作为救援窗口,我个人认为不妥,因为消防救援口应易于从室内和室外打开或破拆,卷帘门不便于破拆。

2.2.3 除有特殊要求的建筑和甲类厂房可不设置消防救援口外,在建筑的外墙上应设置便于消防救援人员出入的消防救援口,并应符合下列规定:    

1 沿外墙的每个防火分区在对应消防救援操作面范围内设置的消防救援口不应少于2个;    

2 无外窗的建筑应每层设置消防救援口,有外窗的建筑应自第三层起每层设置消防救援口;    

3 消防救援口的净高度和净宽度均不应小于1.0m,当利用门时,净宽度不应小于0.8m;    

4 消防救援口应易于从室内和室外打开或破拆,采用玻璃窗时,应选用安全玻璃;    

5 消防救援口应设置可在室内和室外识别的永久性明显标志。

关闭

关闭

手机APP下载