消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

走道净高大于3m的清晰高度和自然排烟窗设置

老师您好,根据GB51251-2017第4.6.9条、4.3.3条,走道净高大于3m的清晰高度和自然排烟窗设置不能设置在净高1/2以上吗?这个对于规范的解读是不是每个省、市不太一样?现在有没有明确的解释?谢谢您

和心 | 2025-05-07 17:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

潘天坤 2025-05-07 20:18 00 [回复]举报

从文字来看,我个人会偏向于走道排烟口可以设置在净高二分之一以上(无论走道净高为多少),不少省份(例如福建省、河南省)也有出台技术文件明确:无论走道净高为多少,走道排烟口均可以设在净高的1/2以上


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准


牛丫头消防课堂 2025-05-07 23:39 00 [回复]举报

应该是你理解有误区,走道不管净空高度多数,净空高度一半以下为最小清晰高度;同时走道的自然排烟窗均可以布置在一半以上即可。

4.6.9 走道、室内空间净高不大于3m的区域,其最小清晰高度不宜小于其净高的1/2。其他区域的最小清晰高度应按下式计算:Hq =1.6 +0.1·H ′

4.3.3 自然排烟窗(口)应设置在排烟区域的顶部或外墙,并应符合下列规定:    

1 当设置在外墙上时,自然排烟窗(口)应在储烟仓以内,但走道、室内空间净高不大于3m的区域的自然排烟窗(口)可设置在室内净高度的1/2以上【图示1】;





萨曼岛的工程师 2025-05-08 08:37 10 [回复]举报

走道净高大于3m,当设置在外墙上时,自然排烟窗(口)应在储烟仓以内;

金灶沐 2025-07-10 10:12 00 [回复]举报

       单一分区走道可以不限烟口在烟层内, 若是靠挡烟垂壁划分n多个分区,挡烟垂壁埋没在烟层中有何意义,划分区又有何意义。

       规范不是说文解字,得有合理的解释。

       不划分区的走道中,规模小功能单一,可以放宽风口高度设置要求,一旦用挡烟垂壁分区,必须考虑到走道布局以及疏散环境的复杂性: 挡烟垂壁存在的意义就是防止烟气蔓延,不能形同虚设(见通规GB55036  11.3.2 );并且走道联通面积越大越不能压低净高,应根据规范反推走道净高 。

       在审查中经常遇到为排烟口按1/2高度计算面积,故意把3米多的净高顺应规范压低到2.9米的情况,其实反而是给逃生增加了困难。

关闭

关闭

手机APP下载