消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

水泵房消防电话

水泵房缺少消防电话,甲方说一直就没有,消防主机有消防电话总机,说是手报插孔电话用的,报告中要不要体现,有没有规范说明?

消防打工人 | 2025-03-17 09:49
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

同同不同 2025-03-17 10:02 10 [回复]举报

6.7.4 电话分机或电话插孔的设置,应符合下列规定:
1 消防水泵房、发电机房、配变电室、计算机网络机房、主要通风和空调机房、防排烟机房、灭火控制系统操作装置处或控制室、企业消防站、消防值班室、总调度室、消防电梯机房及其他与消防联动控制有关的且经常有人值班的机房应设置消防专用电话分机。消防专用电话分机,应固定安装在明显且便于使用的部位,并应有区别于普通电话的标识。

EHS专家-DL 2025-03-17 10:49 10 [回复]举报

《火灾自动报警系统设计规范》GB 50116-2013‌ 中的 ‌第6.7.4条‌规定消防水泵房应设置电话分机或者电话插孔。但我认为消防水泵房、防排烟机房、消防值班室、消防电梯机房等与消防联动控制相关且有人值班的机房,‌必须安装固定式消防专用电话分机‌‌,仅预留电话插孔不符合规范要求

以下场所,规范允许通过预留电话插孔(配合移动电话设备)满足通信需求: ‌手动火灾报警按钮或消火栓按钮旁‌:可仅设置电话插孔(推荐选用带插孔的手动报警按钮)‌;‌避难层‌:每隔20m需设置分机或插孔,若未安装分机但预留插孔,‌需确保插孔可接入移动电话设备‌以满足紧急通话需求‌。

元始天尊 2025-03-17 11:21 00 [回复]举报

50116 6.7.4-1这些场所应设置分机,2-4是说的分机或插孔。

潘天坤 2025-03-17 13:40 00 [回复]举报

不知道楼主说的是维保检测还是消防验收现场查验的第三方检测,是否体现一般要看报告依据是哪些

从国家技术标准来说,消防水泵房需要设置消防电话分机。当如果是既有建筑改造的内容,还有考虑本次是否涉及,如果不涉及是不是可以考虑体现为不符合要求(利旧)

消防打工人   回复: 潘天坤2025-03-19 10:10

维保项目年检

0    0 [回复]举报

关闭

关闭

手机APP下载